step down transformer earth ?
3

step down transformer earth ?

step down transformer earth ?

(OP)
if a step down transformer, 230v/27v ac is used to feed electronics, should the secondary be earthed at one side of the secondary ?

( to help deal with surges, transients, etc )

( obviously the 27v ac is bridge rectified on PCB to 24v dc regulated supply )

thanks

RE: step down transformer earth ?

Not necessarily. In many cases it would be desirable to have a floating secondary supply. If you have serious problems with mains-borne noise coupling through the transformer then you might want to consider an earthed interwinding screen instead.

RE: step down transformer earth ?

3
often time too, 24vdc has its common tied to ground. If this happens with your grounded ac side you will have an instant short of course that blows diodes or fuses.

RE: step down transformer earth ?

Good one, mikekilroy.

I'm a long-time controls guy. We never ground low-voltage transformer secondaries unless we stumble across a really good reason to do so in a particular situation. Ungrounded (floating) is the default. In addition to the 24 VDC power supply troubles (very frequent), circulating currents in the ground bus can lead to the pulling out of one's hair.

Good on ya,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

RE: step down transformer earth ?

IMO the secondary side of the transformer should not be grounded to provide isolation to the main, else the chassis will be considered hot.

If transient noise is a concern, then an isolation capacitor can be put across the primary and the secondary of the transformer.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources