equation for E-field due to current loop
I have an EMI problem to solve. Our 3-ph motor cables have a sawtooth waveform of ~80A pk-pk at 20kHz and ~300V pk-pk square wave (ignoring the low frequency sinusoidal component). The motor is 2m from the driver, with the three cables ~2m long and 5cm spacing each (three side by side). This cable bundle is ~20cm average above chassis. Before coming up with solutions, I need to model the present system and predict what the E-field in dBuV/m will be at 10m distance. This is to show a predicted before-and-after. The radiated fields will be from several sources: the voltage square waves, the current triangle waves and the common-mode current to the motor capacitance. The large currents in this loop have me concerned. The closest equation which I can find in my old textbook is:
E = 120*pi^2*I*A/(wavelength*D), A is cm^2, I is Amps, D is distance to measuring antenna, and the author doesn't say what the units of E is. For a quick estimate I would like to just get a few values at say, 100kHz, 2MHz, and 30MHz assuming the harmonics from the original triangle wave with a fundamental of 20kHz. I'm also assuming we'll be in the ballpark by using 750cm^2 as the average area between each cable and the other two.
Question: Any better formula than the one I've shown above which is in units of dBuV/m?
We need to meet FCC part 47 class-A, industrial location. I have used various solutions in the past but, with much lower current levels. The advice in the thread, <http://www.eng-tips.com/viewthread.cfm?qid=196269&...; from Mark's comment has been useful. The solution will probably be a combination of several of the following methods:
- Shielded cable for each of the three cables (at both ends)
- shield around the three cable bundle
- Cap + snubber from battery return to chassis at the driver
- large ferrite around cable bundle
- cables pulled closer together and closer to chassis
The formula to estimate the current radiated signal strength is what I'm trying to pin down first though.
thanks for the help
thanks for the help