Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...Brilliant! Your site is great...and saving me hours of time at work and making my boss think I am brilliant too! I also picked up on a thread that will potentially save us a lot of money in the future..."

Geography

Where in the world do Eng-Tips members come from?
seanmcc (Electrical)
16 Aug 12 2:03
I need to work out how a transformer arrangement is going to share load. The situation is that there is two 25MVA 66/33KV transformer suppling load to a 33KV bus. The load on the 33KV bus is minimal and does not need back up plan. The transformers also have 7.6KV tertiary windings that supply 7.6KV bus, which is well loaded and needs a backup plan, in the event of a failure. Plan is to use a 33/7.6 transformer, phasing is not a problem, but not sure about load sharing, and do not know how much of the 66/33 impedance will need to be added to the 33/7.6 impedance to work out load share. Simple diagram attached, assume failure of TX2 and operating on TX1 & TX3 7.6KV load share is where I'm not sure, no load share at 33 as only one TX suppling

Not sure where my source is in each case for working out sharing 33kv bus or 66kv bus?

Thanks for you help

Sean
Helpful Member!  prc (Electrical)
17 Aug 12 1:59
Attached enclosure explains the loading condition. In case 33Kv circuit is loaded, then there is a chance of circulating current due to voltgae drop in X1
prc (Electrical)
18 Aug 12 0:49
One more point.Why do you want the 5 MVA transformer to be Dy connected? I think it should be Yd to avoid a star 7.6 kV getting connected to delta 7.6 kV.
seanmcc (Electrical)
19 Aug 12 18:33
PRC
It is not a case of wanting it to be connected this way, more a case of temporary back up using what we have availible until substation is refurbished in 4 years time. We have the two 66/33/7.6 transformers on site, had three there until one failed a couple of weeks ago. 33KV load is not an issue but the 7.6 load is, so looking at our options with out spending large $s. Wanted to understand how the pictured option would work if one of the existing 66 transformers failed and we connected the 33/7.6 as shown.

Seanmcc

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close