LV grid transients - an encore

LV grid transients - an encore

LV grid transients - an encore

(OP)
More than four years ago, I needed to know about real world transients on LV grids. See http://www.eng-tips.com/viewthread.cfm?qid=207168

I am now trying to understand what IEC 60 439-1 actually says. My interpretation is here http://www.gke.org/pub/files/IEC%2060%20439-1%20tr...

But that is a lot more than I or anyone else seems to have encountered IRL. Does anyone have any new experiences? Any recordings of "Killer Transients"?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: LV grid transients - an encore

(OP)
No new data?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: LV grid transients - an encore

(OP)
Invisible? Am I?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: LV grid transients - an encore

FWIW, here in Australia we manufacture electrical safety devices for mining environments and the standards we adhere to require withstanding 75%-120% of the nominal LV line voltage continuously, and 50% for 2 seconds. The only transients considered are dielectric tests - ie. voltage to earth.

For example, here is the LV part of the table for test voltages as required by AS/NZS 2081. It shows the maximum voltage of the power circuit, the power frequency voltage withstand level (1) and lightning impulse voltage withstand level (2). Values for U(m) are in V and for (1) and (2) are in kV.

|U(m)| (1) | (2) |
| 275 | 2.5 | N/A|
| 450 | 3.0 | N/A|
|1200| 4.0 | 10 |

The power frequency voltage withstand is for 1 minute and the lightning impulse is a 1.2/50us wavefront.

But as far as transients phase to phase go, I haven't heard anything about values greater than 120% nominal. But then again, it's not really my field.

RE: LV grid transients - an encore

(OP)
Thanks, Liteyear!
Your answer is in line with our experience. I am beginning to doubt the validity of the IEC 60 439-1 standard. Where, and under what circumstances can such a transient occur?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources