vfd-motor disconnect with early switch
vfd-motor disconnect with early switch
(OP)
I've Eng-Tip'd and googled and searched various vendor sites, but am not finding a suitable disconnect solution. I am using a 3HP 3ph 208v motor controlled by an appropriate VFD, and want to put a manual LOTO disconnect on the load side of the drive. I don't see anything manual with an auxilliary switch, 'early' or otherwise. Is this not a common practice?
I can probably get away with using an electrically actuated switch (contactor), but would prefer manual, and I don't need any bells or whistles (OLP, PLP, etc)...
Thanks
I can probably get away with using an electrically actuated switch (contactor), but would prefer manual, and I don't need any bells or whistles (OLP, PLP, etc)...
Thanks





RE: vfd-motor disconnect with early switch
RE: vfd-motor disconnect with early switch
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: vfd-motor disconnect with early switch
Go to page 23 of this brochure:
"All auxiliary contacts make after and break before the main switch contacts."
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: vfd-motor disconnect with early switch
http://www.hubbell-wiring.com/press/pdfs/H5184.pdf page 11.
PaulBr.
RE: vfd-motor disconnect with early switch
RE: vfd-motor disconnect with early switch
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.