Eccentricity concideration due to reinforcement.

Eccentricity concideration due to reinforcement.

Eccentricity concideration due to reinforcement.

(OP)
I have a tower pipe leg, reinforced with a single angle welded along its length. The reinforcement changes the centroid of the new reinf. leg and thus creates a load eccentricity. When a uplift load is applied to the leg, that extra eccentricity creates an additional moment that has to be taken by the anchor bolts. However, i need to determine if the pier portion of the foundation will have to resist that additional moment. Please see the attached sketch.
As often seen from practice, most towers are built not perfectly in the center of the pier but with some offset due to construction process.

RE: Eccentricity concideration due to reinforcement.

I don't think the eccentricity affects the load in the anchor bolts. What it does is creates a constant eccentricity in the member.

BA

RE: Eccentricity concideration due to reinforcement.

(OP)
what exactly do yo umean by constatn eccentricity? and if eccentricity exist at the connection (i.e. anchor bolts) shouldn't the connection experience the moment?

RE: Eccentricity concideration due to reinforcement.

If the uplift force is centered on the pipe and the pipe is centered on the c.g. of the anchor bolts, the tension is eccentric to the built up column but not to the bolts.

The moment in the column would be P*e from top to bottom but if the connection at both ends of the pipe are hinged, there is no moment transferred to the bolts.

If the pipe is welded to the base plate, the plate would try to resist column rotation, setting up a small moment in the anchor bolt group but it seems to me it could safely be ignored.

BA

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources