for anti-freze system, I thought I read before that it can effect the hydraulic calculations??

If so what should I see in the calculations or what should I ask for to be submitted to show it has been fiqured in??

Thanks

RE: ahj question

If over, I think, 40 gallons then darcy weisbach method must be used. You'll have to reference the temperature expected, the density of the water/anti freeze mix, viscosity (centipoise) at that temperature, etc in the calculation.

Antifreeze can really make a system unworkable at a low temperature, especially a larger system or loop depending on the mixture ratios.

RE: ahj question

(OP)
Thanks found it in the book with your help

Index did not help

RE: ahj question

NewtonFP: I don't think loops are allowed for dry pipe systems unless the latest NPFP 13 allows them.

RE: ahj question

trashcanman,

Loops have always been allowed, grids not.

RE: ahj question

Trashcanman:

The topic is anti freeze systems. We call the anti freeze assembly an "anti freeze loop", at least where I'm from. Sorry for the confusion.

RE: ahj question

(OP)
ok I got a few numbers back and looks like they used them in the hydraulic calcs submitted, any thing to specificaly look for in the clacs?????

RE: ahj question

Make sure that they adjusted the k-factor. Some of the programs don't automatically do that. Make sure that they have selected the proper density and viscosity for the fluid at the low temperature. As stated above, there can be huge swings in pressure demands at low temps.

Other than that, it is pretty straight forward.

Travis Mack
MFP Design, LLC
www.mfpdesign.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources