Dry pipe with attic heads

Dry pipe with attic heads

Dry pipe with attic heads

(OP)
Dry pipe over 500 gallons with attic heads having to meet 60 second rule

Dry pipe by itself being over 500 gallons needs a quick opening device anyway?

And because of the attic heads in use total system still has to meet 60 second rule???

Thanks

RE: Dry pipe with attic heads

If the system is between 500 and 750 Gal, you don't NEED an accelerator. Just that if you don't have one, you need to meet the required water delivery time. Anything over 750 and you need to meet the required time no matter what. I scanned through the tyco datasheets and didn't see anything requiring meeting a certain delivery time where NFPA 13 would not.

RE: Dry pipe with attic heads

(OP)
thanks the "AP" and "BB1 4.5" have delivery times


how about 7.2.3.4 for systems 501 to 750??? I read it to say the 60 second is not required if you have a quick opening device.

using 2010 edition

RE: Dry pipe with attic heads

I missed that in the datasheet, you're absolutely right.

Also correct about the quick opening device negating a specific delivery time. BUT, given that accelerators are generally an in-stock item and fairly easy to plum into the dry trim after the fact - I don't buy an accelerator and have the boys trim the dry valve without it. When it comes to test time, we snap the inspectors test open...if the water gets there in under 60 seconds, bobs your uncle and thanks for the $350 savings. If the water doesn't get there in time, send an apprentice over to the supplier and pick up an accelerator. A good journeyman can plumb it into the trim in less than 1 hour, and we're no worse off than when we started.

RE: Dry pipe with attic heads

(OP)
thanks then will write the comment that way 60 sec or provide device, except where attic heads require it.

reviewing 16 different apt buildings

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources