Concrete Ceiling - Is it safe during a tornado?
I'm not 100% sure this is the right place to post this question but I have to start somewhere. I recently bought an early 1900's, 2 story farmhouse. There is a small room (8'X 8') on the east end of the basement. The ceiling in this room is a concrete slab. The room sits directly below an old enclosed porch and the ceiling is about 10 inches lower than the rest of the house. My question is, first of all, what would been the purpose of a concrete ceiling? And two, would this be a safe place to take shelter in a tornado? It would seem like it to me but my concern is that it could potentially backfire and the ceiling could collapse in the event of a severe tornado. I'm attaching some photos. I would appreciate any advice I can get. Thanks!
RE: Concrete Ceiling - Is it safe during a tornado?
Similar construction is the FEMA requirements for "safe cells". Usually, the design recommended is to use a reinforced 8" concrete slab supported by either 8" reinforced concrete walls or 8" reinforced concrete block walls. The criteria is to provide protection from debris and projectiles with no penetration since it is a life safety issue. The recommendations are based on many years of actual testing at a Texas University. These recommendations apply for "safe cells" within a structure (below or above grade) or for remote structures that are buried or partially buried. Obviously, it is not practical to design individual cells from from a structural standpoint, so the engineers used a performance-based criteria for individual elements. AS far as debris, whatever goes up, comes down, either vertically or horizontally.
Your 10" slab should be adequate, but the amount of reinforcement is unknown, but the 8' spans are short. The question is what are the materials for walls? It is not a typical structural design. since no codes really apply and proven performance is the key for a once in a lifetime event.
Because the FEMA standards are based on life-safety, they contain very specific details that are somewhat unusual. One key item is that the steel door should open into the room to allow egress in the case of a collapse of the adjoining structure.
Search for "safe cell" on the FEMA site for some very interesting study.
Dick
Engineer and international traveler interested in construction techniques, problems and proper design.
To know for certain you'd need to hire a structural engineer to come in and evaluate the pros and cons of your space, explain the relative risks of the space and even perhaps determine the load capacity of the ceiling/walls. They could also offer recommendations for things you can do to add to the safety such as blocking-in the window.
Good luck finding a structural engineer with a knowledge of the practical effects of a tornado shelter since he would be in uncharted territory since there are no standards or codes to use as a guide for F3 to F5 tornadoes. Finding and engineer to evaluate the strength of the slab and connections, but for a cellar the very short term wind has little effect on the walls if the roof of the cell is intact.
The lack of practical engineering knowledge is the reason that the "safe cell" concept (semi-prescriptive) is based on the properties of the acceptable elements and gives a guide to survival. The suggestions (not a code or requirement) are definitely over the top, but provide a practical guide to increase the ability to provide life safety. That is the reason it is used for safe cells within a new frame structure that often are also used as a large closet or a bathroom.
Dick
Dick
That isn't true - check out ICC 500. It is a "code" and provides explicit design requirements for wind forces from tornadoes and hurricanes.
All of FEMA 361 and ICC 500 are based on designing for tornadic activity and provide guidance for tornado wind/pressure forces (250 mph wind) as well as guidance for projectile resistance.
With a window above the ground level (per the photo) the wind loads DO have an effect on the brick walls. It would be stupidity to just ignore that.
Earlier you stated, "Obviously, it is not practical to design individual cells from from a structural standpoint," - I disagree with you - I've designed numerous tornado shelters based on applied wind forces and pressures both under FEMA 361 and ICC 500. It is practical and done all the time.
To keharrisuiuc: Many engineers know these documents as well as other literature out there - so getting a structural engineer to review you situation is a good step.
I erred when I used the word "practical" when I should have been stated that it is not practical because very few engineers would be able to justify the billable hours for a detailed analysis for a small hole in a 100 year old farmhouse wall that for the most part is subjected to much greater loads from the soil since the exception/hole in the wall has little to do with the ability of the "ceiling" to withstand very short term loads and impact. The opening is still an obvious point to consider when it comes to vertical loads and the strength of the members forming the opening if the slab is bearing. When it comes to safety, filling the opening with more masonry is compatible when you add some ventilation, if needed.
The analysis of windows in basement walls for long term loads is possible and has been beat to death for years even without considering the actual fixity. It is a fun, classic problem to analyze when there is nothing else to do since feel people could justify paying the cost in the real world. I first did it 40 years ago because there was nothing else to do and was encouraged to do so because it was similar to the problems we had designing concrete instrumentation building downstream from rocket test stands, but my time was paid by corporate, NASA and the Air Force. - One of the perks you get when employed by multiple sources that want the time used in the best way.
Dick
Please go review it on the icc website: ICC 500 link
The rest of your post makes no sense to me. It seems to suggest that engineers simply can't design a storm shelter.
That is ridiculous.
Mike McCann
MMC Engineering
http://mmcengineering.tripod.com
http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."