Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...Your site is a great idea. I should have joined your site years ago. Better late than never..."

Geography

Where in the world do Eng-Tips members come from?
mustafahh (Mechanical)
29 Jul 12 0:59
Hello everybody,

One of my coworkers brought this question to me. Based on what should we set the time delay for rotating equipment emergency shutdown is there specific standards on the API, ISO or whatever ?
For example, some compressors are set to shutdown if the vibration exceeds the specified shutdown limit if it stays for 3 seconds. Other machines are set to trip if vibration continues for 5 seconds and so on.

Thank you,
electricpete (Electrical)
30 Jul 12 11:34
I have an old standard (API 670-1993 - Vibration, Axial Position, and Bearing Temperature MonitoringSystems) which implies 100 milliseconds max from detection to initation of shutdown

Quote (API)

3.5.1.1.p. The time required to detect and initiate an alarm (alert)
or a shutdown (danger) shall not exceed 100 milliseconds.

So I think using any time delay to try to avoid spurious trips is not a generally accepted approach. Some alternate strategies to the same end may include:
1 - voting logic which trips only if the signal is seen by 2/2 or 2/3 or 3/4 etc.
2 - Standard FMEA circuit review
3 - suitable selection of setpoints, including alert to operators to allow investigation prior to shutdown in many cases, as well as trip setpoint not so low that it trips during normal expected system transients.

=====================================
(2B)+(2B)' ?

JJPellin (Mechanical)
30 Jul 12 21:55
We have machines with trips designed with delays between zero and 30 seconds. There is no standard that I am aware of that dictates the delay. We use an analysis method that considers the risk associated with a failure to trip or a spurious trip associated with all of the potential causes. If a delay can reduce the risks associated with the spurious trip while still retaining the protection needed for the real trip, then a delay is acceptable. But, this analysis is needed. Do not accept a zero delay to reduce secondary damage to equipment if the increase in spurious trip risk will result in danger to personnel.

As already noted, use voting schemes where practical to reduce the spurious trip risk. But, for a real event such as a trip of the main lube oil pump, you may need to consider adding a delay to allow time for the auxiliary pump to come up to speed and avoid a unit shut down. This is especially true if the unit shut down involves some inherent great risk to personnel.

A delay can be used to allow a system to make it through a transient event that would not necessarily create a hazard greater than the hazard associated with the trip. It can give the control system time to regain control. Every situation must be analyzed individually.

Johnny Pellin

mustafahh (Mechanical)
31 Jul 12 0:30
electricpete & JJPellin, thanks for your response.

Is there any logic where we can rely on such as machine speed or HP ? I think the time delay should be less for higher speed machines. But I don't have any clue for that.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close