Rolling Sphere Lightning Rod
(OP)
Is there some way to perform IEC-62305 rolling sphere lightning rod analysis without the use of software? There must be some method that people used when there were no computers.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Rolling Sphere Lightning Rod
|
RE: Rolling Sphere Lightning Rod
IEC 62305-1 Table 6 the minimum peak current and the rolling sphere radius according to LPL class.
The Rrolling=10*I^0.65 m [I[kA].
You may check the rolling spheres contain no equipment [or other element] on a drawing [or sketch].
RE: Rolling Sphere Lightning Rod
in contact with higher portion of roof.
For protection Level-1 ,radius of protection is 20mtrs.
If I have a building of height 90mtrs,how Rolling sphere can cover this.I mean,on vertical height??