maximum PT cable horizontal curve
Where is that requirement in the code? For example 1 to 6 slope. Thank you.
RE: maximum PT cable horizontal curve
To misquoote a famous saying from "The Octopus" ...
"Whatever the hairpins will bear."
Mike McCann
MMC Engineering
http://mmcengineering.tripod.com
I don't think it's in the code. Looks in the PtI post tensioning manual if you are in the US.
Don't know of any code that specifically deals with the detailing of PT tendons. If you look at this document by an Aussie mob who do a lot of PT work locally, page 7 has some guidance for curves and kinks.
www.ptia.org.au/Documents/Practical%20Prestress%20...
You can also look at
pci journal JR 303
Behavior and Design of Post-Tensioned Girder Anchorage Zones
William C. Stone, John E. Breen
p. 36 and following. (Multistrand Side Face Failure Mechanism)
I am trying to find an electronic view of this.
Thank you all.
PTI manual gives some direction. They give 1:6 slope or 10m radius if I remember right. I called VSL with a similar question and they thought the 10m radius was fine