What the best system to start large synchonous motors driving pumps?
Hi folks,
We need to specify a system to start large synchonous motors driving water pumps. The motors are between 5 to 13 MW at 6.9kV. They are feed by a transformer 230/6.9kV, two motors per transformer.
Is the SCR soft-starter the best system for this application?
Thank you in advance for your reply.
Best regards,
Herivelto S. Bronzeado
Brasília, Brazil
Best regards,
Brasília, Brazil
RE: What the best system to start large synchonous motors driving pumps?
A solid-state reduced-voltage for a 13,000 kVA motor is going to be expensive. LCI adjustable frequency drives are probably still a viable option for motors this size.
Then if you start to consider the possible benefits of varying the speed to match flow requirements, the next level up, a VFD, might be worth considering as well. LCIs are of course VFDs, but tnot the most efficient ones if running below full speed, so a CSI or VSI might be a better choice.
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
we balanced the cost of the solid-state soft start versus the cost of an autotransformer-based system.
I am expecting good results.
old field guy
Good luck with that...
Cheers!
Herivelto
Best Regards,
Ministério da Integração Nacional - MI
Brasília, Brazil
Curious about your distinction between LCIs and CSIs. Always believed one was a subset of the other.