Substation Rock Resistivity

Substation Rock Resistivity

Substation Rock Resistivity

(OP)
We are empirically testing substation rock spalls for resistivity and come up with around 10,000 ohm-meters of resistivity. The IEEE80 uses a typical example of 2500 to 3000 ohm-meters for substation rock resistivity. Are we way off base? Our samples are 1-1/2" drain rock.

RE: Substation Rock Resistivity

The resistivity values of 2000 to 3000 Ohm.m referred in your post is for crushed rocks in wet conditions.

For dry conditions, the resistivity value is much higher in the order on million (10^6) Ohm.m.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources