Reinforcing Dowel Placed In Fresh Concrete

Reinforcing Dowel Placed In Fresh Concrete

Reinforcing Dowel Placed In Fresh Concrete

(OP)
Hi All,

I have a situation where the contractor installed reinforcing dowels after the concrete was placed in the wall, rather than installing the dowel and placing concrete afterwards.

I cannot find information regarding this situation - whether the codes allow this, and if so what would the calculated tension capacity be? It would seem to me it would be less than if cast in.

Thanks for any information to shed light on this.

Regards,

Beamman

RE: Reinforcing Dowel Placed In Fresh Concrete

You might try doing a search in the forum here using "wet set anchors" and see if any of the strings can help. Ths has been discussed here before many times.

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: Reinforcing Dowel Placed In Fresh Concrete

If there was no vibration done after setting, it is likely that there are air pockets around the wet set bar, so capacity is likely compromised in this situation.

As far as determining that capacity, I haven't seen any number put to it. I would think you could lose a fair amount of bonded length, so it could just be a reduction in Ld or Hef for calc purposes. Tough to put a number to though.

RE: Reinforcing Dowel Placed In Fresh Concrete

I have seen it done several times. I don't like it at all but I think that I have seen somewhere that it is okay. Probably not in the correct location.

RE: Reinforcing Dowel Placed In Fresh Concrete

If the dowel is required to be fully developed in tension, it should be tied in place and the concrete vibrated around it. If it is just a nominal dowel to resist shear, it is probably okay.

BA

RE: Reinforcing Dowel Placed In Fresh Concrete

I agree with BAretired. ACI section 7.5.1 has verbiage requiring reinforcing be placed and secured before pouring though.

RE: Reinforcing Dowel Placed In Fresh Concrete

(OP)
Thanks to everyone that replied. You confirmed my suspicions regarding this. Thanks PMR06 for the ACI reference.

RE: Reinforcing Dowel Placed In Fresh Concrete

Can you definitely establish that the bar is at the right depth? Horizontal bar? Vertical bar(s)?

It probably did not settle/get pushed all the way down thorough the slab to the very bottom where it will be exposed to corrosion from below, but was it evenly depressed so it is at the right depth all the way on its length?

A bar placed before the concrete is poured has to be suspended "up" from the form, but here, what held it up so it didn't droop too far down in places, but was too shallow in other places?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources