chilled water system tests

chilled water system tests

chilled water system tests

(OP)
hi every one
what is the most important parameter to test and verify when commisioning chilled water system
what is the most pratical way measuring the flow in each loop?

RE: chilled water system tests

Most important, at least for me, is all safety interlocks and devices are in place, properly sized, and operating as intended.

Most practical way of cintinuously measuring loop flow is with a flow meter. Measuring differential pressure drop would be as important, or even more so, as it would go along with factory equipment safety interlock. If commissioning, the easiest way is to ask the TAB subcontractor.

RE: chilled water system tests

(OP)
thank you urgross
what type of flow meter(s) has to be installed?
is it common pracice to measure the flow to each fan coil unit?

RE: chilled water system tests

Absolutely, you need to balance flow at each fan coil unit. Typically, all you'll need is a differential pressure gauge, and the knowledge that multiple trips around the loop will be required to get things set up correctly.

RE: chilled water system tests

Pumpmann, the chiller should maintain a consistent CHW system supply temperature, at set point, across varying loads and flows required by the system. That is its purpose in life. Staging means/methods also needs to be verified and adjusted if necessary if there are two or more chillers.

For flow measurement, the balancer should set flow to design values at each balancing valve. For commissioning, you should spot check flow by running pumps at full speed (forcing open some loads), recording DP across pumps, and verifying flow approximates what is shown on the pump curves.

RE: chilled water system tests

You need also to verify if there is leakage in the chilled water pipes.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources