How to determine the # of heads in a branch line and # of brach line in a remote area?

How to determine the # of heads in a branch line and # of brach line in a remote area?

How to determine the # of heads in a branch line and # of brach line in a remote area?

(OP)
Hi guys,

I'm trying to determine how many heads ina remote area. For emample, 1500 sq.ft. remote area:
is it
- 1.2 x square root of 1500 = 46.48 ft (distance parallel to branch line)

- how do you determine the distance perpendicular to the branch line?

is this how you guys determine the remote area? Thanks in advance..

Newb

RE: How to determine the # of heads in a branch line and # of brach line in a remote area?

1500 / 46.8. That is all you do, unless I am missing something with your question. Just make sure you are at least 1/2 the distance between heads and branch lines with your numbers.

Travis Mack
MFP Design, LLC
www.mfpdesign.com

RE: How to determine the # of heads in a branch line and # of brach line in a remote area?

see NFPA 13 2010 ed

FIGURE A.22.4.4 Example of Determining the Number of
Sprinklers to Be Calculated.

You need to know the max spacing of the sprinkler based on the hazard as follows

Table 8.6.2.2.1(a) Protection Areas and Maximum Spacing of Standard Pendent and Upright Spray Sprinklers for Light Hazard

Table 8.6.2.2.1(b) Protection Areas and Maximum Spacing
of Standard Pendent and Upright Spray Sprinklers for
Ordinary Hazard

Table 8.6.2.2.1(c) Protection Areas and Maximum Spacing
of Standard Pendent and Upright Spray Sprinklers for Extra
Hazard

****************************************
Fire Sprinklers Save Firefighters’ Lives Too!


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources