Load factors in ACI 318 1971

Load factors in ACI 318 1971

Load factors in ACI 318 1971

(OP)
we are checking a concrete floor built in 1974.
The current load combination is 1.2DL+1.6LL from ACI 318.
I am wondering what they used in 1974. 1.4DL+1.7LL?
we do no have a copy for ACI318 1971. Can anyone help me out?
Thanks.

RE: Load factors in ACI 318 1971

I have ACI 318-63 but I don't know if that would have still been in effect in 1974. It specified:

U = 1.5D + 1.8L
or
U = 1.25(D + L + W)
or
U = 0.9D + 1.1W

BA

RE: Load factors in ACI 318 1971

I believe you can purchase ACI 318-71 online for $25.

BA

RE: Load factors in ACI 318 1971

Be aware that some of the capacity reduction factors may have changed as well.

RE: Load factors in ACI 318 1971

Or you can pay $163.50 (http://www.cement.org/buildings/resources.asp?cat2...) and get all from 1908 tom 1999.

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.

RE: Load factors in ACI 318 1971

If you can wait until Wednesday, I have ACI 318-71 in my office. But I'm on vacation now.

RE: Load factors in ACI 318 1971

(OP)
JedClampett
Thank you. Please let us know the load factors and the reduction factor of ACI 318 1971

RE: Load factors in ACI 318 1971

(OP)
I did some research online and found a paper talking about the load reduction factors of earlier days.
Please see the attached pdf.
According to the paper (to calculate the overall or global factor of safety, line 12-18), we can solve these two equations to find the load factors
a*D+b*D (=L) = 1.72*0.9*2*D
a*D+b*D/2 (=L) = 1.67*0.9*1.5*D

then a=1.4, b=1.7

Somebody please verify those load factors if you have ACI318 1971. Thanks.

RE: Load factors in ACI 318 1971

ACI 318-71
U = 1.4D + 1.7L

RE: Load factors in ACI 318 1971

(OP)
Thank you for the verification.
I am very curious now. why are those load factors used in cocnrete (in such earlier days) while ASD were used for almost all other materails?
Does that come from a tradition or the ACI 318 committee just adopted some research paper using load factors? Does anybody know the particular reason?
Sorry, too many questions.

Thanks.

RE: Load factors in ACI 318 1971

My guess is that the failure mechanisms of concrete used with LRFD were:
1) Easier to calculate
2) Easier to match with test data
3) Someone had to be first.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources