Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...I think this forum rocks it has saved my bacon many many times..."

Geography

Where in the world do Eng-Tips members come from?
ciy (Electrical)
5 Jul 12 5:00
There is a power system, one Generator connected to 13.8kV Bus and one Step-up transformer 69/13.8kV primary side connected to the power grid, secondary connect to 13.8kV Bus.
Both generator and transformer have equipped with NGR for forming a low resistance grounding system.
Choose one of two NDS that be closed for grounding.
In general, the NDS of Generator side shall be closed rather than transformer side.

My question is

Is there anything have to take into account if close NDS of transformer side rather than Generator side.

THANKS!
Helpful Member!  dpc (Electrical)
5 Jul 12 16:11
I really try to avoid the need to switch the grounding resistor. But with the NGR at the transformer, your generator is probably ungrounded until the generator breaker is closed - depending on the location of the generator breaker.
ScottyUK (Electrical)
5 Jul 12 16:16
What is the transformer winding configuration? Normally an HV generator has a high resistance grounding system, possibly using a grounding transformer, to limit damage to the stator core in the event of an earth fault. Ideally the generator would feed a delta winding.

ciy (Electrical)
5 Jul 12 22:02
ScottyUK,The said power system scheme roughly is shown on the attached for reference.

dpc, thanks for your advices!!
From generator protective view, keep NDS closing with generator is good solution.
odlanor (Electrical)
8 Jul 12 10:36
you must install both NGR.
NGR transformer is necessary to keep BUS 13.8kV 2500A 40kA system grounded, when generator is desconnected.
NGR generator is necessary to keep generator grounded, when generator is desconnected but excited with speed no load.
Kiribanda (Electrical)
9 Jul 12 12:55
ciy,
Just for curiosity I am asking this question.
It looks like your Utility had allowed to use a DELTA for the GST on 69 kV side.When there is a ground fault on your 69 kV network the 69 kV line
will trip and isolate from its own ground fault fault protection at the upstream sub.But the generator will continue to feed to the
69 kV ground fault because your GST is having a DELTA connection at 69 kV.How do you trip the generator under that faulty condition? Do you have
an intertrip by a communication line?
ciy (Electrical)
10 Jul 12 4:40
Kiribanda,
In our practice, GST 69kV side is Delta connection and the Utility side is Wye connection.
If transmission line has a SLG fault then the utility trip the circuit at substation.
The incoming CB shall be tripped by undervoltage Relay(27)to separate from the Grid.
At this time, my power system to be a island system to power continuously.
To prevent the Grid to be a ungrounding system, 59Vo Relay is necesssary to reserve.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close