Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...This site is truly a marvel. Without a doubt the most comprehensive, friendly and just plain useful resource of its kind..."

Geography

Where in the world do Eng-Tips members come from?
jmbelectrical (Electrical)
1 Jul 12 12:15
When working on projects that require the use of VFDs, I was always under the impression that the input voltage needed to match the output voltage. Is this necessarily true? I recently worked on a project in which we had specified a VFD capable of accepting a 240-volt, single-phase input and producing a three-phase output. Could such a VFD control a 208-volt, three-phase motor? In other words, can VFDs control motors rated for voltages lower than the input voltage of the VFD?
DRWeig (Electrical)
1 Jul 12 12:41
The input does not need to match the output on a VFD, but the output rating needs to match the motor.

Good on ya,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

itsmoked (Electrical)
1 Jul 12 16:10
Yes Lower.

Keith Cress
kcress - http://www.flaminsystems.com

Skogsgurra (Electrical)
1 Jul 12 16:59
Usually no problem to feed a lower voltage motor. But, when going to extremes, like feeding a 230 V motor from an inverter connected to a 690 V grid (European) it should be remembered that the PWM pulses now have close to 1 kV amplitude and even though the RMS voltage can be set to the motor's rated voltage, it is not at all guaranteed that the insulation of the 230 V motor can withstand the high PWM pulse voltage.

Usually, there is a limit as to how much one can "detune" the voltage. But that limit can usually be overridden and sometimes doesn't even exist.

Be careful. Check what the insulation is designed for before proceeding.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

jmbelectrical (Electrical)
7 Jul 12 19:27
What about a VFD serving a motor rated for a higher voltage? I am assuming that this is not possible as the VFD does not contain any means (A transformer) of increasing the incoming supply voltage. Is this correct?
jraef (Electrical)
8 Jul 12 12:15
Yes, that is correct.

There is a slight exception, only in that some SMALL drives use what is called a "voltage doubler" on the front end to boost the voltage AS IT ENTERS the VFD converter stage. It is a rectifier that then uses capacitors to double the DC side (do a search on "voltage doubler circuit" to see a schematic). The now doubled DC is then fed straight through the rectifier in the VFD direct to the DC bus at a voltage high enough to allow the drive to deliver a PWM AC output at twice the AC input voltage. This is why you see SMALL drives offered here in the US with 115V input and 230V output, where 115V single phase is ubiquitous. Technically, this can be done at any size, and there are at least two mfrs that I have seen which offer this method on larger drives, ie that accept 230V in to run 460V motors. But the caps become ridiculous and a transformer is cheaper, so I don't know why anyone would bother.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close