Step down converter to load cell, current issue?
Step down converter to load cell, current issue?
(OP)
I have a 25000 lb rated load cell that I need to supply with 12Vdc, I have a battery pack that puts out approximately 37Vdc. The resistance in the load cell is 350 Ohms. My concern is that if I step down the battery pack with a converter from the 37Vdc to 12Vdc, what kind of current am I going to be sending to the load cell? My circuit knowledge is prehistoric but will the load cell only draw the current it needs? I don't want to fry the load cell and put my work back 3 months while it gets fixed. I believe I need about 1A and I know that some converters put out 12Vdc with anywhere to 3A-8A.





RE: Step down converter to load cell, current issue?
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
RE: Step down converter to load cell, current issue?
http://www.ebay.com/itm/DC-DC-Converter-12VDC-25A-...
to hook up to your 37 some volts. This will provide isolation and step it down to a regulated 12V. Adding a 68 ohm resistor in series will drop it down to 10V. Measure the voltage to calculate correction factor or play around with resistors till you get exactly 10V.