Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...Your site has saved me hours of work that I cannot begin to express my satisfaction..."

Geography

Where in the world do Eng-Tips members come from?
sudiptoghosh (Electrical)
27 Jun 12 13:28
What is the advantage of a GSU transformer of 11KV/69 KV Connected to a 66KV grid.Why 69 KV is used instead of 11kv/66 KV
cranky108 (Electrical)
27 Jun 12 13:35
In some places 69 kV is a standard voltage.
sudiptoghosh (Electrical)
27 Jun 12 13:38
The system voltage is 66 KV and not 69 KV.Then why the GSU Voltage is 69KV instead of 66KV
Kiribanda (Electrical)
27 Jun 12 13:56
sudiptoghosh,
What is the RATED voltage of your generator unit? Is it 11 kV or otherwise?
sudiptoghosh (Electrical)
27 Jun 12 14:31
11 KV ONLY
Helpful Member!(2)  rcwilson (Electrical)
27 Jun 12 16:24
If the GSU puts out generated power at exactly the system voltage, it will not be able to deliver MVAR's. At best it might be able to achieve 1.0 power factor without exceeding the generator's voltage rating. The GSU voltage must be greater than the system voltage to enable the generator to supply reactive power.

MVAR's (reactive power) always flow from high voltage to low voltage. If voltages are equal no reactive power flows.

63-69 kV is only a 4.3% increase, within the +/-5% typical generator voltage range and GSU tap range.
Helpful Member!  FPelec (Electrical)
28 Jun 12 2:25
I agree with rcwilson,
the use of an higher nominal voltage on HV side of GSU causes a shift of the whole capability curve of the generator along the Q axis.
In other words it will be more easy to supply reactive power to the grid and more difficult to absorb reactive power from the grid.

Si duri puer ingeni videtur,
preconem facias vel architectum.

Helpful Member!  Kiribanda (Electrical)
28 Jun 12 11:17
sudiptoghosh,
In that case one of the objectives of your generator connecting to Utility is to provide voltage support in addition to active power export to the grid.That means
the GSU trafo should have a higher no-load voltage to push reactive power to achieve voltage support as pointed out by member rcwilson.
sudiptoghosh (Electrical)
28 Jun 12 14:52
Thanks to all. But the MVAR will be supplied by the generator and we operate at Lagging Power factor to supply MVAR to the grid.So if the GSU voltage is 66KV instead of 69KV with an OLTC what is the harm
Helpful Member!  GTstartup (Electrical)
28 Jun 12 16:01
As stated before 69kV is more standard so probably cheaper to buy a "off the shelf" GSU and use the lowest tap on the tap changer
rcwilson (Electrical)
28 Jun 12 16:10
As long as the generator and on load tap changer can raise the 66 kV side voltage enough to push MVARs to the utility system, there may not be a problem. You could do the calculations or simulations to verify that the generator voltage will stay within its +/-5% voltage limits for all probable combinaitons of utility 66 kV voltage level and leading / lagging MVAR support.


There may also be some considerations about over excitation (volts per Hz) if the transformer's rated voltage is less than operating voltage. That problem may be coverd in the OLTC tap design specifications.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close