VFD Driven motor efficiency
VFD Driven motor efficiency
(OP)
Hi Friends,
I have a question regarding the overall efficiency of VFD Driven motors. Normally the VFD efficiency is around 96% and motor efficiency around 94% (around 30kW range).
When we made a measurement for a motor used in pumping system, the overall efficiency fell much below the expected, and as a result the contractor is held responsible for the lower efficiecy assuming the lower pump efficiency. The pumps are KSB, manufactured in Germany and factory tested and confirmed to operate at declared efficiency.
Therefore i feel the lower efficiency is due to the VFD / or measurement method
Test arrangement is as indicated below,
* Pump flow is measured with calibrated electromagnetic flow meter at the pump delivery.
* Pressure is measured using calibrated pressure gauges across the pump.
* Power analyzer connected to the input of the VFD.
Inut power is measured and the VFD efficiency of 96% and motor efficiency of 94% is used for the calculation of overall efficiency.
As the input current to the VFD is not sinusoidal, can the current transformer detect the correct current for calculating the power? Is there any other way of doing this test?
Has anyone of you come across a similar situation?
Paliha
I have a question regarding the overall efficiency of VFD Driven motors. Normally the VFD efficiency is around 96% and motor efficiency around 94% (around 30kW range).
When we made a measurement for a motor used in pumping system, the overall efficiency fell much below the expected, and as a result the contractor is held responsible for the lower efficiecy assuming the lower pump efficiency. The pumps are KSB, manufactured in Germany and factory tested and confirmed to operate at declared efficiency.
Therefore i feel the lower efficiency is due to the VFD / or measurement method
Test arrangement is as indicated below,
* Pump flow is measured with calibrated electromagnetic flow meter at the pump delivery.
* Pressure is measured using calibrated pressure gauges across the pump.
* Power analyzer connected to the input of the VFD.
Inut power is measured and the VFD efficiency of 96% and motor efficiency of 94% is used for the calculation of overall efficiency.
As the input current to the VFD is not sinusoidal, can the current transformer detect the correct current for calculating the power? Is there any other way of doing this test?
Has anyone of you come across a similar situation?
Paliha





RE: VFD Driven motor efficiency
1> This will avoid distortion power factor issues which may not be properly handled by your test equipment.
2> The stated pump efficiency is at rated speed and the efficiency may vary at other than rated speed.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: VFD Driven motor efficiency
Your VFD / motor combination assumed efficiencies are pretty good. Make sure your watt meter is a true rms type, or do waross's suggestion and run the pump across the line. You'll need the pump's curves and an accurate speed too.
Good on ya,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
RE: VFD Driven motor efficiency
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: VFD Driven motor efficiency
http://www.binsfeld.com/index.php/products/
RE: VFD Driven motor efficiency
Try checking the efficiency without the VFD in the circuit.
There is no bypass contactor- The contractor is not ready to do a temporary wiring. So it is difficult. .
DRWeig (Electrical) 21 Jun 12 8:50
I'll amplify waross' second statement: Pump efficiency varies a lot with speed. See attached from DOE
Onething i forgot to mention- the test was carried out at 50Hz. Therefore the pump speed is as rated. Thank you for the link.
jraef (Electrical) 21 Jun 12 15:41
In answer to your specific question, yes, harmonics created by the VFD can make conventional metering methods inaccurate for purposes such as this. Many VFDs will display the output kW of the motor, that tends to be very accurate. Then all you have to do is accept the VFD efficiency at face value.
We used VFD display (percentage of motor kW) but the efficiency is still low.
TD2K (Chemical) 21 Jun 12 21:44
Can you install a torque meter on the pump drive shaft and determine how much power the pump is actually using?
No there is no space and the shaft is rotating.
RE: VFD Driven motor efficiency
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: VFD Driven motor efficiency
Such as 3000 RPM rather than 2940 RPM.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: VFD Driven motor efficiency
Pardon me if you've already considered that --
Good on ya,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
RE: VFD Driven motor efficiency
There is a good paper on the subject called "Motors With Adjustable Speed Drives: Testing Protocol and Efficiency Standard" authored by Anibal T. de Almeida, Pierre Angers, Conrad U. Brunner and Martin Doppelbauer. It describes VFD and motor efficiency testing at different speeds and loads. I did a quick search and didn't find a good, but try Googling it.
RE: VFD Driven motor efficiency
Proceedings of the 6th International Conference eemods '09:
Energy Efficiency in Motor Driven Systems
Nantes, FRANCE, 14-17 September 2009
Volume 1
Editors: Paolo BERTOLDI, Bogdan ATANASIU
EUR 24142
Attached is another relevant paper from US DOE.
Good on ya,
Goober Dave