Talk to an electrical engineer and they'll teach you about ground loops. I can tell you only the little I know.
If you have a thermocouple which has its junction connected electrically to its metallic sheath, that thermocouple junction is considered to be "grounded". If the junction is embedded in MgO insulation such that it is in thermal contact but not in electrical contact with the sheath, or the junction is exposed beyond the end of the sheath, that junction is considered "ungrounded". Whenever we have used grounded junction thermocouples in the interest of having the fastest responding and most accurate junction possible, we have very often experienced problems with getting good data out of them due to ground loops or other electrical interference.
If you use a "grounded" junction T/C, what you have to worry about is a difference in potential between the ground that the sheath is connected to electrically (i.e. the equipment) and the ground that the thermocouple amplifier/reading device is connected to (i.e. the instrumentation ground). If there's an isolating transmitter in there, the problem is reduced of course, but ONLY if it has electrical isolation as part of its design. MANY thermocouple input cards for I/O systems do not have proper isolation as part of their design, and hence they are subject to ground loop problems. Of course when the tech comes around and plugs the T/C into his battery-powered (i.e. isolated) thermocouple reader/calibrator, everything looks fine.
EMI/RFI is a different matter. Unshielded wires, particularly unshielded wires connected to a very high input impedance amplifier (such as, say, unshielded thermocouple extension wires connected to a thermocouple reading device) are particularly good antennas to pick up this kind of noise, which can be generated in great quantities by devices such as motor speed controllers etc. Twisting the wires helps to reduce the noise, but a shield helps more still. That shield has to be connected to ground somewhere, but not such that it becomes a ground loop path itself. But it is still necessary to keep the T/C junction isolated electrically from the sheath ground.
Does this make things clearer? |
|