Thanks so much for having a place for us propeller heads to hang out and chat.
Geography
pbrod (Industrial)
18 Jun 12 5:07
We would like to replace our dP measurements for a venturi flow measurement. There are 4 measurement venturi's in a reaction zone measuring the air flow to 4 reactors. It is difficult to connect these new systems with our old DCS system.
Would the following be possible?
- a new dP transmitter on each venturi which has an integrated controller to control the air damper. the set point in m³/h is send to the transmittor/controller (wireless or 4-20mA) from our DCS system.
Is there industrial equipment available to do this (Emmerson, Honeywell,...)
Thanks in advance!
best regards,
danw2 (Industrial)
18 Jun 12 8:04
What and why are things like an analog 4-20 DP transmitter and a damper acutator positioner difficult to connect to your old DCS'? Isn't the wiring already in place?
I'm told Foundation Fieldbus (FF) devices have a PID function block. But when you do things with FF, all the pieces have to be FF: field instrument, valve positioner, DCS. FF is a different way of doing business.
You could always do the pre-DCS analog way: local PID controller, analog DP transmitter, analog valve actuator positioner.
decker1 (Industrial)
18 Jun 12 19:12
ABB makes a nice single loop controler CM30 There is also an option to make it a dule loop controller so it can handle two loops.
http://www.abb.ca/product/seitp330/2b8542f8825150d...
dcasto (Chemical)
21 Jun 12 14:36
fisher ROC flowboss or controlwave can do it
pbrod (Industrial)
22 Jun 12 8:14
thanks for the help!
i keep you informed about our solution (but it can take a while).
thanks again,
regards