AOA,
currently redesigning sprinkler system for high rise building. What section of NFPA codes describes the pipe diametee w.r.t No of sprinklers attached on that pipe?????

RE: Sprinkler

About how many heads, sq ft, floors are you talking about

Nfpa 13 would like it hydraulically calculated most of the time

RE: Sprinkler

NFPA 13 Chapter 11 would be a good starting point.

RE: Sprinkler

There are old pipe schedules found in NFPA 13, that have pipe sizing based on number of heads. This may be what you are referring.

However, there is nothing that limits the number of heads on a line. If you can calc it, you can have as many as you can prove.

Travis Mack
MFP Design, LLC
www.mfpdesign.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources