Single Plate Shear Connection with axial load

Single Plate Shear Connection with axial load

Single Plate Shear Connection with axial load

(OP)
I am analyzing a single plate shear connection with an axial load using AISC 13th edition. During my analysis I stumbled upon criteria 6 on page 10-103 which says "Ensure that the supported beam is braced at points of support" I am not sure what this is trying to say can anyone expound on this an give a better explanation.

Thanks,

RE: Single Plate Shear Connection with axial load

Laterally brace it at bearing points....so it can't roll

RE: Single Plate Shear Connection with axial load

Axial load in a single plate connection has an eccentricity. This must be considered in the connection design as a weak axis bending of the single plate. Unless the beam is restricted from lateral movement, by horizontal bracing, concrete, etc.

There have been several lengthy dicussions of this connection on this forum.

www.FerrellEngineering.com

RE: Single Plate Shear Connection with axial load

Seems like if you have a floor or roof deck laterally supporting the top flange, then that would be sufficient. Right?

RE: Single Plate Shear Connection with axial load

IMHO composite floor with studs on the beam flange would be sufficient. But deck only or roof deck, provides little lateral stability.

www.FerrellEngineering.com

RE: Single Plate Shear Connection with axial load

(OP)
If the distance "a" is less than 3.5" it wouldn't need to be laterally supported at bearing points would it? I would think since this criteria wasn't considered for the conventional configuration for "a" being less than 3.5" than you wouldn't need to worry about this. Or am I wrong for thinking that

Thanks,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources