Gypsum sheathing diaphragm
Good Afternoon All!
I have a little bit of a tricky situation that I am trying to deal with. What I have is a 60' x 100' building made exclusively out of cold-formed members, including the roof trusses. Two sides of the structure are adjacent to a taller PEMB building so wind loads do not apply to those two sides. Based upon the geotech report, it is in seismic category A. The issue I am having is with the diaphragm design. The trusses will have a standing seam roof applied to hat channels at 2' o.c., which is not able to transfer diaphragm shear to the shear walls. Due to the classification of the structure, non-combustible materials are required for all structural elements and therefore to sheet the top chords of the trusses and create a true diaphragm, fire-retardant plywood/osb would be required. Currently, using fire-retardant sheathing is cost prohibitive (approximately $10,000), which is a small drop in comparison to the overall cost, but nevertheless I have been given the task of finding something that works. I have approached the truss manufactures about designing a diaphragm using x-braced strapping at the top chord. They said they can but that it will be quite labor intensive and thus drive the cost up again.
So what I am looking to do is utilize the gypsum ceiling and a series of drag struts to transfer the wind load into a number of interior walls. Thus far I have not been able to locate any information regarding the design of a cold-formed diaphragm which utilizes gypsum. Does this idea sound like it may work? Am I missing something easier or is this method in violation the 2009 IBC? As it stands now, using 6 interior walls as shear carrying walls, I can get the diaphragm maximum shear down around 100 plf.
RE: Gypsum sheathing diaphragm
Even if there is no literature on light gauge with gypsum, it seems you could use wood framing/gypsum diaphragm numbers as long as your fasteners have a least the same shear resistance as the wood/gypsum fasteners.
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
Jim
BA