On a typical system with an expansion tank, the make-up water line connection point to the chilled water system is the point of zero pressure change. The pressure at this point is the same whether the pump is running or not.

I'm guessing this holds true for a system without an expansion tank.

In your case, the pressure drop on the pump suction, when the pump is energized, should be the same as the water pressure drop (friction, loss through valves, etc.) from the make-up water line connection point to the pump suction.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources