Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...I've gotten solutions within a day - it saved a lot of time and actually got me one ATTABOY from my boss..."

Geography

Where in the world do Eng-Tips members come from?
TransPlanner86 (Electrical)
7 Jun 12 8:48
I anm trying to figure out what is good utility practice for performing generator interconnection studies on distribution systems. I have a situation where there is so much generation on the distribution system that there is a concern about backfeeding to the transmission level and overloading the distribution transformer (115/33kV).

The utility is using spreadsheet to deteremine the loading on the transformer. They just totaled up the maximum capacity for all of the generators (no historical factor or diversity factor) and then subtracted the minimum load. They also did not include any losses or run a power flow analysis to include those losses in calculating the bank loading.

1) Please me know if you would include the losses and/or us a power flow program to do this analysis.

2) Would you use historical factors or diversity factors for the existing generation?

Thanks!
rterickson (Electrical)
7 Jun 12 18:21
The interconnection studies should be rigorous enough to identify all of the impacts that the new generation will impose on the utility. The study should identify all of the costs that the developer needs to agree to before construction. If you miss some of the impacts, you will be on the hook for them later.

It's not clear what size transformer you are referring to, load (MVA) is important to know.

If the generation is high enough, then certainly losses and transmission/distribution power flows should be evaluated. I don't see anything particularly wrong with considering all of the generation and load to be coincident.

Might be worthwhile to Google "distributed generation interconnection requirements" to see how other utilites approach it.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close