Phase-Earth voltage in an ungrounded system during fault

Phase-Earth voltage in an ungrounded system during fault

Phase-Earth voltage in an ungrounded system during fault

(OP)
Can anyone confirm what readings I should be obtaining when testing for voltage phase-earth on a system which is ungrounded and has a ground fault. 440v phase-phase in normal operation. Would a voltage of 440v to earth indicate a ground fault or would you expect zero volts in the grounded phase and upto 173% in the others phase to earth.

If anyone can confirm please

RE: Phase-Earth voltage in an ungrounded system during fault

It's easier to visualize if you use a delta system as your example. If you ground one of the phases, the voltage at that point is 0 volts. The other two phases maintain the phase to phase voltages, which in this case are the phase to ground voltages.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources