How does one calculate opening /closing time in control butterfly valve & on -off butterfly valve
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: opening/closing time
Opening and closing time are usually estimated or calculated for several purposes:
a) To avoid water hammer (liquid pressure peaks) that will damage equipment. The pressure peaks might under wrong circumstances (too abrupt closing) be well over allowed pressure limits for the equipment. Searching general on net and/or all forums here for keywoords 'water hammer' you will find several references to calculations and estimating methods.
b) To be well within suitable figures for the mechanical equipment (electrical, pneumatical or other orbiturators normal operating standards). Figueres after manufacturors recommandation, process consideration and for regulating valves to give well damped opearations. To high frequency regulations and abrupt movements to be avoided. 'As long as possible' or normal for equipment often sought rather than fastest.
c) To satisfy emergency shutdown valves need to shut down fast. Often for larger valves and water regulated in two steps: for instance 70-80% fast, rest slower to avoid water hammer. Mechanical: producers linits. Pipeline calculations as point a.
RE: opening/closing time
Note that a butterfly valve could have 80% flow when only 20% open. This is a generalisation as it butterfly valves have different characteristics form onemanufacturer to another. The point is butterfly vavles are not good for control purposes. Often two speed opening is used.
"Sharing knowledge is the way to immortality"
His Holiness the Dalai Lama.
http://waterhammer.hopout.com.au/
RE: opening/closing time
That said you can do some empirical testing, to get an indication of the time it will take and use the Cv values of the various controls in the circuit as a guide. Basically the higher the Cv the faster the unit will operate!
However, and this was the impetus for writing, when considering fail safe actuator (spring return) generally the client will want the fail (spring) stroke to be optimised. To keep that stroke to a minimum (i.e. be quick) keep the air supply to a minimum! If the actuator is sized to work on 60 psi, only use 60 psi. If you have 100 psi of air in the cylinder it is doing nothing but adding time to the fail stroke; if the valve has happily operated with the 60 psi all you have done is add a useless mass of air which only has to be exhausted before the actuator can begin to react. More in not necessarily better!
Rant over.
RE: opening/closing time
If spring return actuator failure is required to have a slow operation fit a speed reducer to the SOV exhaust port.
“The beautiful thing about learning is that no one can take it away from you.”
---B.B. King
http://waterhammer.hopout.com.au/
RE: opening/closing time
Noted, but you would be surprised at the number of times I have been asked: "Why doesn't this react more quickly?" when the first few seconds are spent just waiting for the excess pressure to evacuate from the cylinder! I don't know, maybe it is counter-intuitive to think that less supply pressure = more rapid response (and most of the spring return valves I have been involved with are on ESD service, and shutting, no matter what, is the criteria) but it has been a thorn in my heal for a while.
RE: opening/closing time
“The beautiful thing about learning is that no one can take it away from you.”
---B.B. King
http://waterhammer.hopout.com.au/