is this possible? A co-worker is telling me all i need to do is install a neutral conductor midway between the 220v leg.
Thanks.
b
Thanks.
b
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
generating 110v from 380/220v system
|
RE: generating 110v from 380/220v system
RE: generating 110v from 380/220v system
In the UK, the center point of the wye is the neutral. no question.
Even when a 220 Volt transformer is used for 220 Volt single phase loads, one end of the winding is grounded and by convention is called the neutral.
If 110 Volts is needed it may be derived from a center tap on the 220 Volt transformer (if there is one present).
So we can have a single phase circuit (or one phase of a three phase installation) where one end of a 220 Volt winding is grounded and by convention called the neutral. 110 Volts may then be supplied from a center tap on a 220 Volt transformer.
We will have 110 Volts to ground/neutral and 220 Volts to ground/neutral.
The AHJ may not accept this arrangement.
And I agree with David. You may use a center tap to derive 110 Volts but you can not call it a neutral.
The transformer may need to be overload protected on the primary side.
With the single phase gen-sets a two pole breaker was used to protect both 220 Volt lines.
These sets were reconnected to North American standards before use.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: generating 110v from 380/220v system
The situation is i have 11kV and am stepping down to 380/220v via a transformer.
Thanks.
b
RE: generating 110v from 380/220v system
If you use three single phase 220 Volt transformers AND one or more have a center tap at 110 Volts you may supply 110 Volts, subject to local codes.
If you are using a three phase transformer you may not have 110 Volt taps.
Perhaps someone from the UK may add something.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: generating 110v from 380/220v system
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: generating 110v from 380/220v system
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: generating 110v from 380/220v system
The UK does tend to use 110V centre-tapped transformers (55V-0-55V) as a reduced risk source of power for the construction industry. Most professional portable tools are designed to run on this supply.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: generating 110v from 380/220v system
The explanation was that in the UK, 220/380 Volts in wye configuration is standard with the wye point as the neutral and grounded. When a single phase transformer was used, one end was grounded and by convention called the neutral. The center tap was a 120 Volt tap and not a neutral.
It was a glitch that we straightened out. The suppliers were good people and we had no further issues with a good number of gen-set purchases and installations.
I was aware that 110 Volt tools were in use but I was not aware that the supply was 55V-0-55V.
Thanks again for the information.