Punching holes in angle
How close to the inside radius can a fabricator punch a hole? I have 7x4x.375 angle and a architect wants a 1" slotted horizontal hole at 1.5" up from the heel of the angle. I am not sure that can be done.
RE: Punching holes in angle
Call the fabricator??
AISC Manual 14th Ed, Table 1-7A gives workable gages in angle legs. For 4" leg, the gage is 2 1/2". For 7" leg, it's 4" for one fastener or 2 1/2" & 3" for two fasteners. The foot note says that other gages are permitted to suit specific requirements subject to clearances and edge distance limitations.
AISC Manual 14th Ed, Table 7-15 gives entering and tightening clearances for conventional bolts. For 1" dia bolt, the minimum distance to the center of the hole from the fillet is given as 1".
That's right at the edge of what our shop could do with our Anglemaster. If I really need it I can get 1 1/8" from the inside of the angle. They prefer 1 3/16". Never had an issue using the AISC dims referenced by DST.
From what I understand though, there are a lot of variables. Punch size, angle thickness, equipment capacity, offset punches. I don't believe our machine can handle 7" angle so it might be totally different for a machine that can.