Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...Really appreciate your site. Really good site for learning what others do when they run into problems. You guy's are great!!!..."

Geography

Where in the world do Eng-Tips members come from?
Wilbur55 (Mechanical)
27 May 12 22:11
The test port on the water service shut-off is shown on the upstream side of the valve in this detail:

http://www.cityofwpb.com/engineering/standards/2007_Details_PDFs/WATER_SERVICE/WS-10.pdf

Why would that be? If the tap is left open/leaks/etc., then turning off the valve at the connection to the city main would be required for any remedy.
bimr (Civil/Environmental)
28 May 12 15:22
Test cocks are in place to attach test equipment for evaluating whether the double check assembly is still functional. According to the Ninth Edition of the Manual of Cross-Connection
Control, when testing the double check valve assembly, the tester wants to determine if each of the two check valves holds the minimum acceptable value of 1.0 psid in the direction of flow. Refer to the link for further testing instructions.

http://www.usc.edu/dept/fccchr/Crosstalks/ctsp98.pdf

One would assume that the bypass is used to pressurize the discharge side in order to test the check valves and the pressure is released at the upstream test port.

The double check assembly is for irrigation service such as lawn sprinkler systems and swimming pools at single family residential units and would not normally be used 24 hours per day and may be shut down at any time for maintenance.

The double check assembly is different than a Reduced Pressure Zone Device (RPZD, RPZ or RPZ valve). The RPZD is a type of backflow prevention device used to protect water supplies from contamination. RPZDs may also be known as reduced pressure principle backflow prevention devices, or reduced pressure zone assemblies.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close