multin 489 protection relay

multin 489 protection relay

multin 489 protection relay

(OP)
what type of protection tests can one carry out on multin 489 relay, which test equipment shoud one also use

RE: multin 489 protection relay

What do you mean protections tests ?

Look at the GE literature and it will mention everything you need to know.

RE: multin 489 protection relay

Hello,

I recommend you to read the manufacturer manul, they typically explain what to do.

However, I think that at least you shold test the following:

1) CTR, inject 1 A and the reading on the relay screen should match according to CTR
2) Test all the functions you have enabled and each one of them should close or open the relay contacts, as well as turn on the leds on the relay' screen and also an event on relay memory should be recorded.

Brst Regards

RE: multin 489 protection relay

If you are in the USA, you need to follow NERC guidelines. If there is a previous set of test results test what has been tested in the past, thus establishing a protocol. GE has a commissioning checklist in the manual, if you choose to follow their guidelines. Whatever you do, be consistent! Make sure your test equipment is calibrated and traceable.

As mentioned above, test all analog inputs (voltage and current). Test all contacts for proper operation.

As far as what equipment you need, at least a source with 2 currents (dif), voltage, variable phase angle and frequency. It also needs to have a timer. You will also likely need the GE SW which is free and available on GE Multilin website. You can rent test equipment, or if this is beyond what you want to invest, hire a qualified service company.

RE: multin 489 protection relay

Don't forget to also test the PT's and CT's once you've tested the relay.

RE: multin 489 protection relay

Test the enabled elements with a Doble 6150.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources