multin 489 protection relay
what type of protection tests can one carry out on multin 489 relay, which test equipment shoud one also use
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: multin 489 protection relay
Look at the GE literature and it will mention everything you need to know.
I recommend you to read the manufacturer manul, they typically explain what to do.
However, I think that at least you shold test the following:
1) CTR, inject 1 A and the reading on the relay screen should match according to CTR
2) Test all the functions you have enabled and each one of them should close or open the relay contacts, as well as turn on the leds on the relay' screen and also an event on relay memory should be recorded.
Brst Regards
As mentioned above, test all analog inputs (voltage and current). Test all contacts for proper operation.
As far as what equipment you need, at least a source with 2 currents (dif), voltage, variable phase angle and frequency. It also needs to have a timer. You will also likely need the GE SW which is free and available on GE Multilin website. You can rent test equipment, or if this is beyond what you want to invest, hire a qualified service company.