Bolt Design for Ledger Beam
3

Bolt Design for Ledger Beam

Bolt Design for Ledger Beam

(OP)
I have a 3 x 12 bolted to masonry wall for floor framing. Can someone verify the single shear value of a 7/8 bolt. Any tips will greatly appreciated. I have a value of 495 pounds but it seems low. Thanks

RE: Bolt Design for Ledger Beam

What is the species and grade of the ledger?

RE: Bolt Design for Ledger Beam

(OP)
It will be Doug Fir Large Grade 2 or better

RE: Bolt Design for Ledger Beam

Masonry wall might be controlling?? But 500 lbs actaully doesn't seem unreasonable - but haven't checked.

RE: Bolt Design for Ledger Beam

I get 1010 pounds for the ledger itself, but don't have the latest values for masonry.

RE: Bolt Design for Ledger Beam

(OP)
I think the block reduces the value around 50% but not sure.

RE: Bolt Design for Ledger Beam

No, it doesn't work that way. Problem is, I don't have the latest masonry code. The 1010 pounds is the minimum value of all possible failure modes of the bolt in the wood ledger by itself.

There is a separate check for failure mode in the masonry. If the masonry is uninspected, the allowable stress is reduced by half but that is not applied to the 1010 pounds wood value...it is applied to the bolt value in masonry.

Is this regular solid-grouted CMU at least 8" wide? Also, the bolt needs to be 6" into masonry.

RE: Bolt Design for Ledger Beam

@Cap4000 : Ref: ACI 530-05, Section 2.1.4.2.3 - Allowable Stress Design of masonry
The allowable load in shear primarily depends on the strength of masonry, edge distance of anchor from
top of the masonry, and area of anchor.
Assuming min. strength of masonry as 1500 psi and fy for steel as 36000 psi, I get the following values:

edge dist. from top of masonry ----- Allowable load in shear
10.5" ---------------------------------------------- 1917 lbs.
8" -------------------------------------------------- 1412 lbs
6" -------------------------------------------------- 1009 lbs
4" --------------------------------------------------- 605 lbs
3" -------------------------------------------------- 403 lbs

The minimum effective embedment length of the headed and bent-bar anchor bolt shall be 4 bolt diameters, but not less than 2".

RE: Bolt Design for Ledger Beam

Most large anchor suppliers, Hilti, Simpson, Fastenal, etc can supply you tables that fit these exact requirements.

RE: Bolt Design for Ledger Beam

The American Wood Council has an online calculator.

http://www.awc.org/calculators/connections/ccstyle.asp

I think it's appropriate to use concrete as your main member type, although I don't what their assumption is for dowel bearing strength in the masonry. The only reference I've ever found is the 1997 NDS, Table 8.2E, which gave a dowel bearing strength of 6000 psi for >= 2000 psi concrete or for masonry. It probably doesn't matter, as Mode IIIs will likely control.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources