High pressure in standpipe system
Being a prairie guy, I don't do a lot of sprinkler/standpipe systems in high rises. This means I don't deal with >175psi too often. Designing a system for a 36 story, two stair condo at the moment, and I am looking at very high pressures at the lower levels in order to hit 100psi @ 250gpm at the top of the most remote standpipe (while flowing a total of 750gpm).
The most obvious solution would be to separate into two vertical zones of high and low pressure using a large pressure regulating valve set to 175psi in the basement. However,
NFPA 13-2010 7.2.4(3) mandates that the failure of a pressure regulating devices cannot allow high pressure to more than two hose valves. Is there any way around this requirement short of installing 2 1/2" prvs + 3" drain riser up the tower until static falls below 175? Has anyone installed two large pressure regulating valves in series to meet this requirement?
My strategy is to feed the lower floors before the pump, and use steel pipe and 250 psi standard spray heads until pump churn + city static drops below 175 psi. I will then continue up with blaze pipe and res sprinks to the top.
Any advice from the high rise pros here is appreciated!
Thanks in advance,
Steve
Thanks in advance,
Steve
RE: High pressure in standpipe system
I had always heard that these valves fail closed when they fail. If that is true, putting them in series would not be the best. If that is not the case, then series would be fine.
Travis Mack
MFP Design, LLC
www.mfpdesign.com
Maybe I am just not picturing it correctly in my head.
Thanks again for the help.
thread184-263835: >175 psi sprinkler system
thread184-299740: Pressure Reducing Valves
Related info...
http://www.usfa.fema.gov/downloads/pdf/publications/tr-082.pdf
http://www.cla-val.com/pdfs/B-Fire_Products_Brochure.pdf