(2) ausphil (Electrical) |
16 May 12 23:01 |
The other thing you need to clarify is the actual VLF test you are using, and the usefulness of this test for the failure modes that occur in the cable you are looking at.
Is it just a high voltage withstand test? If you are just doing a HV withstand test, I would question why you would want to take out a cable at MV that is performing, and subject it to an overvoltage, which may cause the cable to fail, which may be a hard to find fault because it only had the capacity of the test set cause the damage (as opposed to having the power from the system break down the fault and make it much easier to find). Also, passing a HV withstand test doesn't necessarily give you any idea of the condition of the cable for the medium or long term in service, it really gives you the confidence that it will not fail on energisation or soon thereafter ( a condition that you have only subject the cable to just to perform your test).
Are you measuring power factor or tan delta with the HV test (to try to determine water tree activity)? This measurement gives an average of all the problematic and good sections of the cable. If you assume that your cable has grown its problems evenly, then it may be helpful to determine if you want to replace it or not, but it cannot determine the location of a poor 50m of cable in a run of 5km, it may not actually even detect it.
Are you measuring PD in conjunction with the HV test? If you measure PD in your cable during an overvoltage test, this may be of use, but you then must be able to locate it to make it of value. Some estimations of PD tree growth with VLF show that PD would lead to a failure in XLPE within the test period at a multiple of the system voltage. The problem can be, if I have multiple location of PD activity, I will have grown all trees at all locations, but only one of them will have grown to failure. Once this one is repaired, I must retest, and I will grow the next longest tree to failure, and I will keep doing this until I have many joints in the cable - has this increased reliability, or deacreased it with many more points for moisture entry and human error. Also, the PD may only be present at high overvoltages, and not be present at normal system voltages. So, in actual fact, you may need to have many years of switching and lightning overvoltages causing PD activity for very short times before the cable actually fails.
You must work out what failure mode you are trying to detect, then determine which test is useful in detecting this failure mode, and then work out what you are going to do with the answers.
At MV, I would only be pulling a cable out of service to do any sort of test on it if it is absolutely system critical. Otherwise you may actually be unnecesarily shortening the life of the existing insulation by this "intrusive" test.
Ausphil |
|