DC circuit breaker selection question for PV application

DC circuit breaker selection question for PV application

DC circuit breaker selection question for PV application

(OP)
Hi All,

Here is a question coming from Ontario Canada.
I am trying to size the DC breaker and conductors for a Solar application.


The short circuit of the PV source circuit is calculated at 200A dc, 600Vdc

the ampere rating of the PV source circuit is 200Ax125%=250A dc

the continuous load of the PV source circuit is 200Ax125%=250A dc


The selected 600V DC circuit breakers carry standard 80% rating.

The frame size of the CB is rated at 400A.

Can I select a thermal-magnetic trip unit at 250A (=the continuous load), and select the conductor size greater than 250A?

Or I need to select a trip unit at 350A (which is the next plug size greater than 312.5A=250x125%), and select the conductor size greater than 350A?

Thank you very much for all the help!!!!!

Best....Jake

RE: DC circuit breaker selection question for PV application

A standard breaker can technically CARRY 100% rated current, but per most rules you size the conductors at 125% of the FLC then you size the breaker to protect the conductors, so the breaker ENDS UP carrying only 80% of it's rated capacity. So when a breaker mfr says that the breaker is rated for 80% FLC, they are saying that the trip calibration and heat dissipation design is based on that expected use. You can order a breaker that is "100% rated" which generally just means different calibration of the trip unit and sometimes different lugs, but then there are other rules to follow when you do that and restrictions on the conductors you must use etc.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources