Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...Many thanks to you for putting it together and to the forum members for taking the time to post their replies and give their time to help others. Their isn't another site that can touch it..."

Geography

Where in the world do Eng-Tips members come from?

Treatment of emergency standby generators in short circuit current calculation studies

BHENG (Electrical)
10 May 12 13:17

Hi all
I was wondering if there is an explicit statement in our professional literature (NEC, IEEE, IEC) about treatment of emergency standby generators (e.g. in AUTO mode) when calculating short circuit currents.
Are we allowed to ignore contribution from those machines?
Cheers
BH

waross (Electrical)
10 May 12 13:28

Standby sets are normally offline and have no effect on normal short circuit currents.
When online, the SC current from the generator is typically so much less than the grid short circuit current that reliable coordination may be an issue. The standby generator may not supply enough current to trip breakers on instantaneous. While waiting for an inverse time trip rather than an instantaneous trip, voltage collapse may occur with more issues.
Often the issue may be not enough SC current to ensure reliable operation of protective devices with settings based on grid SC currents.

Bill
--------------------
"Why not the best?"
Jimmy Carter

dpc (Electrical)
10 May 12 13:52

I agree with Bill if the purpose of the short circuit calculations is to determine adequacy of equipment ratings. However, if you are doing arc-flash calculations, you cannot ignore the generator. It is necessary to calculate arc-flash levels for both operating conditions and then take the worst-case of the two.

BHENG (Electrical)
10 May 12 14:04

Thanks for quick replies...I see an installation where the primary backup generator is being backed-up (with an identical machine)...both on AUTO mode and several seconds of time delay between loss of utility and loss of primary generator.
What is the right fault current calculation method? If the main controller fails - it is theoretically (and practically) possible to have all three sources feeding the load bus!
Re the arc flash calculations...what do you suggest?
BH

dpc (Electrical)
10 May 12 14:54

Unless the two generators have synchronizing capability, only one can be connected to your loads at one time.

waross (Electrical)
10 May 12 20:04

Closing in a second source without synchronizing gear is theoretically possible but practically impossible. You have about a maximum window of 60 degrees out of 360 for an unsynchronized closure to succeed. Plus or minus 30 Degrees out of 360 is a 5 out of 6 chance of failure. I have seen successful closures at 30 degree error but that may well be outside the envelope of many installations. 15 degrees plus or minus is more than many operators would be comfortable with. Closing in a second source takes the odds to 1 in 36. Theoretically possible but practically impossible is a good description.

Bill
--------------------
"Why not the best?"
Jimmy Carter

davidbeach (Electrical)
10 May 12 23:16

How are they switched? Typically with an ATS it is physically impossible to have both sources at the same time. With paralleling gear, on the other hand, the whole point is paralleling the sources. For equipment ratings, assuming an ATS, I'd completely ignore the generator. If there's paralleling gear, you have to consider both in parallel, and the fault current, particularly for SLG faults, of both paralleled can be significantly higher than the sum of each alone. For arc flash you have to look at each and every case. Often the generator alone, with much lower fault currents, will produce a far higher hazard due to much longer clearing times.

BHENG (Electrical)
11 May 12 9:28

The whole scheme utilizes paralleling gear (circuit breakers and some simple relaying scheme - i.e. no ATS).
My concern is that no robust PLC control is in place and long control wiring running hundreds of yards between various relay panels is so unreliable (in long term), consequently an undesirable switching arrangement is quite a possibility (especially taking into account a very large number of machines connected together). Could anyone suggest a reputable specialist consultant to help re this issue?

dpc (Electrical)
11 May 12 11:20

Quote:

Could anyone suggest a reputable specialist consultant to help re this issue?

If you told us your location perhaps you would get a better recommendation. This is an international forum.
waross (Electrical)
11 May 12 21:45
Try e3ach parallel setup as a stand alone unit. One generator and associated synchronizing and connecting gear. Then send a single signal to each unit when it is to go online. Keep all the controls other than a two wire external signal local to the paralleling contactor or switch. Then a fault on the external circuit will commend the set to make a proper and orderly connection top the bus. No harm done. Similarly an open in the external control circuit will result in a fail to connect condition. Again no harm done.

Bill
--------------------
"Why not the best?"
Jimmy Carter

living2learn (Electrical)
15 May 12 16:25
I have had many installations where the generators contributed more fault current than the utility. It consisted of very large generator plants that paralleld upwards of (5) engines onto a common bus. The zero sequence current available from generators seems to be pretty low compared to the sub transiant and had two different instances when the SLG fault was over 200kAIC.

Off topic, but when I utilize closed transition transfer switches which do parallel the sources I always add the fault contribution from both sources.

Food for thought. Always do the calcs...

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close