600/1000v cable for 690V IT system

600/1000v cable for 690V IT system

600/1000v cable for 690V IT system

(OP)

Are you permitted to use 600/1000V grade cable on a 690V IT system that would run with earth fault for >8hrs? or should you use 1900/3300V cable?

RE: 600/1000v cable for 690V IT system

I don't think the Electricity Supply Regulations in any country permit the use of this system with one phase
grounded for public supply network.
For UK see BS7430 ch. 4.3(c):
"An IT system has the source either unearthed
or earthed through a high impedance and the
exposed-conductive-parts of the installation are
connected to an electrically independent earth
electrode (see Figure 2). Attention is drawn to the
requirements of the current Electricity Supply
Regulations, which do not permit the use of this
system for public supply networks in the UK."

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources