I'm looking for guidance on edge distance less than 4d when load is applied perpendicular to the grain of a timber member. All the NDS in C11.5 states is that they don't specifically address this issue.






RE: NDS less than 4d edge distance
If you do, you are stepping outside of the standard of practice for wood design per the building codes which reference the NDS as a standard.
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
RE: NDS less than 4d edge distance
One recent project comes to mind where the shear studs on a steal beam were only 1-1/2" above the steel decking. The engineer took a reduced capacity/stud and continued on. This was in clear violation of the AISC but the EOR bought off on his justification.
RE: NDS less than 4d edge distance
That being said, if you need a number (for forensic engineering or something) the dowel bearing equations can give you something. I'd expect it to overestimate the capacity, but it is a starting point.