Quick question:
If you use a generator (say 750kVA) as a power supply, stepping up through a 500kVA transformer with around 5% impedance, then try to DOL start a 180kW SC motor hooked up to a fan. Will the generator see a significantly lower startup current than if a 1500kVA 5% impedance transformer is used?
If you use a generator (say 750kVA) as a power supply, stepping up through a 500kVA transformer with around 5% impedance, then try to DOL start a 180kW SC motor hooked up to a fan. Will the generator see a significantly lower startup current than if a 1500kVA 5% impedance transformer is used?






RE: DOL starting motor, 2 dif sized txf's
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: DOL starting motor, 2 dif sized txf's
RE: DOL starting motor, 2 dif sized txf's
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: DOL starting motor, 2 dif sized txf's
I don't see many sophisticated breakers on a generator of that size. The breaker is probably a thermal magnetic which is tripping on instantaneous current.
The instantaneous (magnetic) trips may be set one notch higher.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: DOL starting motor, 2 dif sized txf's
the generator has to trip as the overload will be more than 80%[minimum,depends on voltage drop].