In North American Utilities, what is their minimum power pfactor requirement at the PCC of industrial plant main substation?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Utility Imposed Minimum Load Power Factor
|
RE: Utility Imposed Minimum Load Power Factor
RE: Utility Imposed Minimum Load Power Factor
Any load customer with a pf lower than 0.90 automatically starts paying 'penalties' based on the standard regulator-approved demand tariff.
There is not generally a 'required minimum' unless the customer(s) in question have a large enough load and a poor-enough pf that the distribution system is affected (and the large demand 'penalties' quickly pay for utility-side capacitors if the customer's arithmetic skills are poor. We generally advise customer's about the amount of money they are leaving 'on the table' via bad pf)