Utility Imposed Minimum Load Power Factor
In North American Utilities, what is their minimum power pfactor requirement at the PCC of industrial plant main substation?
RE: Utility Imposed Minimum Load Power Factor
I think you'll find it varies by utility.  For our installations, we pay a penalty for every kvarh below a PF of 0.9 (the first 0.1 of PF is free). The penalty for excess kvarh is $0.0014/kvarh, and only applies to facilities that draw greater than 400 kW.
The typical way to assess bad power factor in Canada is to charge ALL demand-rated customers for monthly peak demand by charging the GREATER of (90% of measured kVA, 100% of measured kW).
Any load customer with a pf lower than 0.90 automatically starts paying 'penalties' based on the standard regulator-approved demand tariff.
There is not generally a 'required minimum' unless the customer(s) in question have a large enough load and a poor-enough pf that the distribution system is affected (and the large demand 'penalties' quickly pay for utility-side capacitors if the customer's arithmetic skills are poor. We generally advise customer's about the amount of money they are leaving 'on the table' via bad pf)