Sprinkler main (w/ no outlets) running though electrical room

Sprinkler main (w/ no outlets) running though electrical room

Sprinkler main (w/ no outlets) running though electrical room

(OP)
I am designing a job with 4 sprinkler systems. The mechanical room is next to the electrical room and the chase that 2 of my systems go into is on the other side of the electrical room.
Can I pass through the electrical room with the 2 mains if there are no outlets or couplings on the mains in that room?
I heard there are provisions for this but I cant find them in NFPA.
Any help would be appreciated!

RE: Sprinkler main (w/ no outlets) running though electrical room

I would not pass through the elec room, but .... if you insist, the NEC provides guidance.  You have to take special measures (sheet metal, with a drain, etc.) to catch any leaks from the spkr piping.  Check the NEC.

RE: Sprinkler main (w/ no outlets) running though electrical room

When allowed. If the water in the pipe is relatively cold (relative to the humidity of the environment) the condensing moisture in the pipe would drop, so it is recommended to pass the pipes under cable trays for example.  

RE: Sprinkler main (w/ no outlets) running though electrical room

so how about nfpa 13:::

is the room meeting 8.15.10.3????????????

8.15.10 Electrical Equipment.   

8.15.10.1    Unless the requirements of 8.15.10.3 are met, sprinkler protection shall be required in electrical equipment rooms.



8.15.10.2    Hoods or shields installed to protect important electrical equipment from sprinkler discharge shall be noncombustible.



8.15.10.3    Sprinklers shall not be required in electrical equipment rooms where all of the following conditions are met:


(1)
The room is dedicated to electrical equipment only.


(2)
Only dry-type electrical equipment is used.


(3)
Equipment is installed in a 2-hour fire-rated enclosure including protection for penetrations.


(4)
No combustible storage is permitted to be stored in the room.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources