Voltage Transformer name plate
2

Voltage Transformer name plate

Voltage Transformer name plate

(OP)
I have a voltage transformer name plate said

6,3/√3 / 0.11/√3 / 0.11/3
0.2/3P / 40/30 kVA

can someone explain about this values?

thank you

RE: Voltage Transformer name plate

The first set of values are voltages, given first in Line to Line, then √3 to denote the Line to Neutral Voltage.  

So 6.3kV/√3 = 3.637 kV on the primary.  The same applies for the secondary voltages, here also expressed in kV.

.110 kV = 110 V/√3 = 63.51 V.  These are pretty standard secondary ratings for PT.

The reason for the  0.11/√3 /  0.11/3 listing is that the PT has 2 secondary windings, which is fairly common.  Do I read correctly that the second winding does not have "√3" attached to it?

This is an IEC PT, so I will guess that the 0.2/3P is 0.2 = metering accuracy and the 3P is the protection accuracy.

The 40/30 kVA, would require a little more investigation as the numbers don't appear to add up for a 3 winding device.  Perhaps it is intended for secondary windings only.

I would look for the manufacturers data sheet to confirm the kVA ratings and the lack of √3.





 

RE: Voltage Transformer name plate

(OP)
thanks a lot for your explanation smallgreek
I'm pretty sure that the name plate say 110/√3 / 110/3
that's what confuse me, is it the secondary voltage too? but why 110 / 3 instead of 110 / √3
it is uncommon value of secondary voltage.
I couldn't find the manual book, and by the way it is chinese PT

RE: Voltage Transformer name plate

Is the second winding meant for a broken delta connection perhaps?  That could explain the sqrt(3).

RE: Voltage Transformer name plate

(OP)
Can you explain more about this broken delta connection? what's the purpose and I still not clear about the 110/3 V
thank you very much

RE: Voltage Transformer name plate

2
It's used for detecting earth faults on impedance- or un-earthed systems.  During a phase-earth fault, the voltage developed across the broken section of the broken delta would be 110V on a 6.3/sqr(3):110/3 set of VTs, or 190V on a 6.3/sqr(3):110/sqr(3) set of VTs.

See http://www.basler.com/downloads/pc-59n01.pdf, or google for further explanation.

RE: Voltage Transformer name plate

(OP)
thank you very much mgtrp for your explanation

RE: Voltage Transformer name plate

I agree with mgtrp on the 3V0.  What is this 110/3 winding connected to?  If you can verify that it is a broken delta connection, is there a properly sized resistor in the circuit?

There is more information on the VT subject from a more IEC perspective available @  http://www.cigre.nl/media/40320/06_current-___voltage_transformers.pdf  This also explains the accuracy class, which was part of the nameplate data you listed in the first post.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources