14400:120 PT fuse change

14400:120 PT fuse change

14400:120 PT fuse change

(OP)
silly question from a green horn.  anyone familiar with a load break device to pull this fuse hot?  or would the common recommendation be to take an outage.  this is on a manufacturing facility that would love to avoid an outage.

also, what have you seen as likely causes for PT fuses to blow?

thanks in advance.

RE: 14400:120 PT fuse change

In some kinds of metal clad 15kV switchgear, the PT is mounted in a roll out drawer, which pulls the entire PT+ fuse assembly out.

For outdoor applications I have seen hot stick removal.

What kind of PT and where is it located?  Have you made any attempt to determine why the fuse is blowing?  I would not want to be the person inserting a fuse into a faulted PT.

See the recent thread http://eng-tips.com/viewthread.cfm?qid=320853
on the possible reasons for a blown fuse.

RE: 14400:120 PT fuse change

Why would you need a load break device to remove a blown fuse? If the fuse is blown there is no load.

RE: 14400:120 PT fuse change

Strongly recommend against replacing a blown VT fuse with the system energized.

It's impossible to tell if it's a fuse failure or a problem originating from the VT itself. Closing a fuse into a damaged/faulty VT could be dangerous.

Need to check out the VTs prior to trying to re-energize, e.g. megger test, ratio test, and possibly excitation test (if you have comparative results).

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources