Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...(I) have been able to get my problems solved from past messages and also new posts that other users have responded to promptly..."

Geography

Where in the world do Eng-Tips members come from?
ekuegler (Electrical)
2 May 12 15:25
Wondering if anyone can help here.

We have an ABB ACV700 VFD, supplied by a 690vdc bus, 690vac to a step up transformer to 2600vac supplying a downhole ESP motor. Drive currently operating/running - however pump discharging very little....? Hertz = 3.5-4Hz, ref = -25.7 and current 413A. This is very unusual, drive has not tripped and no alarms indicating, what could be the cause of such unusual readings?????
MiketheEngineer (Structural)
2 May 12 15:55
It's broken??
KllrWolf (Electrical)
2 May 12 17:08
How big is the motor you are running?  What is the normal running current?  How long has the system run normally before this happened?

It does sound like the VFD is really off at only 4Hz.  That would mean the motor is only running at 120 RPM.  If that is correct, it means very low flow.  It would also mean at that speed you will very quickly destroy the bearings in the motor.

If the current is correct and the VFD is in error for the frequency, you may be running the motor/pump backwards.  This really only applies if the system is just being commissioned or electrical work was done and the wiring got swapped. Switch 2 phases from the motor side of the transformer and recheck.    
jraef (Electrical)
2 May 12 17:32
There are any number of possible issues and you have not provided anywhere near enough information.

Was this system engineered to work together or did someone assume it was going to work fine? If it was engineered, have you spoken with the engineer?

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close