Transformer Tap settings

Transformer Tap settings

Transformer Tap settings

(OP)
Electrical system study with all loads connected showed we need to modify primary Taps to -5% to maintain voltage. Currently, most of the loads are not connected, and bus voltages at MV level is around 4300v. If Taps are changed now, voltages might get over 4500v, which is high. First, would a higher voltage like that hurt loads? What is the best approach when it comes to changing transformer Taps? Should we do that now, or add loads slowly and see what that does?

RE: Transformer Tap settings

From the post,it is assumed that taps are on HV for HV variation.So for constant primary voltage if you change to minus tap,transformer will be overfluxed to that extent with higher secondray voltage.If the tap changer is of on-load type,tap changing need to be done only when secondary voltage dips.Whether overvoltage hurts the loads- it depends on the type of load.

RE: Transformer Tap settings

(OP)
Thanks for the reply. I guuess what I was trying to ask is, what is usually the bus voltage range recommended by standards?

RE: Transformer Tap settings

In the UK the declared range is +/- 6% on nominal for a public utility supply. You'll have to check the equivalent regulations for yuor location.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Transformer Tap settings

Permissible voltage ranges are given nin standards. eg ANSIC84.1-2006, IEC 60038-2009
For Nominal voltage of 4160 V, the permissible range is 4370-4050 Volts as per ANSI

RE: Transformer Tap settings

(OP)
Thank you guys...that was helpful!

RE: Transformer Tap settings

It is advisable to perform a turns ratio test after changing taps.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources